V0N_hydro,
Yes, I agree, it's a very nicely done job. A lot of thought looks to have gone into it. However, a couple of things to note or advise on...
V0N_hydro said:
...Too bad the redundant supply only comes in 24V and not 125VDC...
I assume you are using the 1756-P
B75R redundant power supply, which is 24VDC supplied? There is indeed a 120/240VAC 50/60Hz supplied option, the 1756-P
A75R redundant power supply.
You can read the specs here on page 13...
"
1756 ControlLogix Power Supplies Specifications" -
1756-td005_-en-e.pdf
V0N_hydro said:
...the 17 slot chassis *just* fit the width of the panel between the corner ducts ...
The minimum required spacing for ControlLogix chassis can be read here on page 5...
"
1756 ControlLogix Chassis Specifications" -
1756-td006_-en-e.pdf
The standard power supply for the ControlLogix in your 2nd screenshot looks to be ok, as the required spacing for the power supply from the sides of the enclosure must be a minimum 10.2 cm, or 4 inches, and can
include the wireway.
However, in your 3rd screenshot, even though you have used a chassis adapter to make it *just* fit, it is not of the required spacing for a chassis adapter. There is specific mention of this on page 5...
"
When you mount a ControlLogix chassis with a redundant power supply and a chassis adapter module in an enclosure,
follow these spacing requirements.
The 10.2 (4.0) measurement to the side of the enclosure
can include the wireway only on the right side of the chassis."
This means you should have at least 10.2cm, or 4 inches, between the chassis adapter to the left, and the wireway,
not the side of the enclosure.
The cable between the 1756-PSCA2 chassis adapter and the redundant power supply is completely inside the trunking. This cable is a "
1756-CPR2 - Redundant power supply cable (Length = 0.9 1m [3 ft])". It is designated Catagory 3 wiring. You are instructed to follow the "
Industrial Automation Wiring and Grounding Guidelines" -
1770-in041_-en-p.pdf to properly route your cabling, according to its designated Catagory, to avoid noise.
On page 2, the guideline defines Catagory 3 as...
"
low-voltage dc power cables — provide backplane power to the system components"
On page 3, Table B gives general guidelines for routing different Catagory cables away from each other...
"
Category 3 - Route conductors external to all raceways in the enclosure or in a raceway separate from any category-1 conductors with
the same spacing listed for category-2 conductors, where possible.
So, ideally, the 1756-PSCA2 cable should be outside the trunking. You have it inside, ok, but are there any Catagory 1 conductors with the Catagory 3 cable in the trunking? If so, are the routing guidelines for Catagory 2 satisfied i.e. 6 inches from Catagory 1 conductors? This is not likely in what looks like a 4 inch trunking?
Also, The 1756-CPR2 cable can have a maximum bend radius of 12.7cm, or 5 inches. Is your wireway 5 inches wide? If only 4 inches, then, as you have the chassis adapter tight against the wireway, the bend radius may be tighter than 5 inches.
The spacing requirements are "required".
The routing guidelines are "guidelines" only for noise immunity.
That brings me on to a very important point with regard to the above. The spacing requirements are important for heat dissipation. Normally, if there is not sufficient surface area, and a cool enough external air temperature, for heat dissipation through convection, then ventilation is used to assist the heat dissipation. I'm not saying you do not have any, but I don't see any sign of ventilation in your screenshots? You have a lot of heat sources in some of those enclosures. Regardless of whether you have tight chassis spacing or not, what in general is cooling these enclosures? Perhaps there is some form of ventilation that I cannot see? If so, then please feel free to correct me.
I'm not being picky here, your enclosures look fantastic, it's just if "something" turns to smoke down the road, then RA, or A.N.Other, will throw all this stuff at you, plus it's good practice either way.
I used to sub-contract to a panel builder years ago, and he sometimes lost bids on projects just because he wanted an extra enclosure added, or to use a larger one, rather than try stuffing things in where they really ought not to go. Some also decided that ventilation was a luxury. On a couple of occasions we went back to sort out some of "told you so" ones, finding they had to run with the doors open in the Summer, and 3PH cooling fans in front of them on the floor!
Very impressive, all the same VON_hydro
Regards,
George