Thanks Norm.
The yellow component is a three-phase monitor from TimeMark. If three-phase 480 is present, it has a switch that closes. I use the input from that switch to allow the program to call the motor controls on.
We use brown, orange, yellow (BOY) for 480 3-phase. I don't remember where I saw it first but we've been using it for the ten years I've done this type of work.
The drives are not protected by anything except the Main Disconnect which is a 60A breaker. We have been in discussions recently about protecting these drives. In a previous panel I had added onto, we protect three 1HP motors on a 10 breaker (X3 for a total of 9 motors), but I'm not sure that's how I want to do it here. I've seen motors protected by fuses but that allows for single-phasing the motors running on contactors. The PowerFlex drives have built-in overload protection. We will ultimately answer the VFD protection question.
The breakers at the top of the panel provide field device, Panelview, and PLC protection/isolation. The relay bank in the center of the top row will ultimately be replaced by a relay card in the PLC Chassis. The fuses to the right of the Main Disconnect protect the 480/120VAC XFMR mounted outside the right of the panel.