control valve feedback on plc
plcpapam
Oct 2010
ENGLAND
have one controlvalve (fail close) use on steam line for flare area configured & operate in vendor plc when force from plc to open it's open after open when i test poer fail(remove power cable) it physicaly going close but in plc still showing 100% open plc side status not going change ...so my quastion is do plc side also shoiuld some indication come like BAD MODE....COMMUNICATION FAIL...or something that indicate valve condition power fail or failure mode...cause maintainance guy how khow valve now close cause power fail ..m doing loop check...
How does the PLC control the valve ?
Analog output to valve positioner? to I/P (current to pneumatic transducer)?
Digital communications to valve positioner?
Does the valve positioner provide position feedback?
- via analog 4-20mA ?
- via digital comm?
Thanks for interest, valve have digital 6010 series emerson positioner no feed back connected limit switch nothing ...just two wire from plc ...it's control valve but they using like on/off valve..my interest is if valve is in open condition & suppose power fail ( iop) so valve going its fail safe condition close shut off...so that same time what will be effect u can showing in plc ( i mean plc have also status 100% open logical 1) but actually in field it closed ( logical 0) so do there plc will change status in ladder logic from 1 to 0.....or is there green healthy line become red like now it's not helathy ...my interest is to khow what effect will on plc side if valve fail it's communication (power fail,,,,calbe some open...or sort somewhere)...
Hello, I am a part-time machine builder that has recently been exposed to the world of PLC controls. I subbed out the controls for my latest...
17
5,323
Hi all. I've got a new requirement I've never run into before. I'm being required to read control valve position feedback back the PLC. In the...
8,833
I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
432
So I'm pretty green when it comes to troubleshooting in the field so bear with me. We have a Danfoss valve that opens/closes from an analog output...
23
982
Hi there, We have a system at a water treatment plant where large raw water tanks feed into the plant that's all on the same level. At high tank...
18
3,801