ControlLogix PLC/SLC Messages with Octal Addressing?
sanger
Nov 2005
Toronto
172
Quick question.
When using the CLX PLC/SLC Message Mapping to map files 0 (Output) and 1 (Input) to CLX Integer registers is it smart enough to convert the requests for addresses in Octal to Decimal?
e.g. If we have File 1 mapped to tag 'Inputs', when a PanelView program tries to read I:10/17 (old PLC-5 address) will the Message Mapping automatically convert that to a read of Inputs[8].15 or will all the I and O addresses in the Panelview need to be adjusted?
That is a really good question !
And I have no idea.
My guess is that the conversion would be transparent because the PanelView would (probably) perform a 16-bit Word-sized Read command. I don't think there's even a PCCC command for reading a single bit value.
The hex value of the bit offset is the same inside the 16-bit word no matter if you express it in Octal or in Decimal.
But that's just a guess. It's equally possible that the ControlLogix will consider the question moot by not supporting data files 0 and 1 in the Map PLC/SLC Messages feature. I've only ever started with data file 3.
Is this a PanelView Standard, or a PanelView Plus ? What network is the PanelView using ?
We did a test and it correctly converted the requests in Octal from the PV to the decimal requests in the ControlLogix.
Is this even possible? I was trying to read a SLC mapped Timer ACC over DF1 (PCCC) and I get an Illegal address. My thought is maybe it doesn't...
1,237
I have a customer with a Data Highway system that uses it to tell the case conveyor that it palletizers infeed belt is running and that a full...
4,792
Guys, I am new in Allen Bradley PLCs, I need to setup the "Path to PLC Processor Module" in an OPC server configuration for each of my equipment...
10,251
85
Hi everyone i have a customer, who wants to show an alarm on the machine, if the I/O forces are enabled and set, on at ControlLogix L81E with...
273