Hi,
we have a machine with a ControlLogix rack and 2 EN2T network cards in that rack. One is for the normal Ethernet/IP subnet (192.168.11.xxx), for all the Point-IO, Kinetix, Powerflex,...
The second network card is a different subnet (192.168.0.xxx) which is for communication to a Automation-PC.
Right now we have a remote access solution which makes it possible to get an IP out of the 192.168.0.xxx subnet to reach the PLC and the Automation-PC.
But it´s only possible to go online with the PLC. All the other devices in the 192.168.11.xxx are not reachable. But this would be very helpful for webserver diagnostics, Powerflex parameter change...
I´m not a really informatic specialist, but is there a solution to get a bridge to the 2. Ethernet card with the 192.168.11.xxx network?
Thank you very much for your replies!