Hello im working on a project with a panelview 600 and a flexlogix connected thru controlnet.
panel uses plenty of scheduled tags, so i decided to use unscheduled, the problem is that i get the 634 error and the strange thing is that scheduled tags works fine.
Read fail.*
Communications warning
PanelView is communicating with logic controller.
The data table address does not exist. Check/define data table address in the logic controller.
In RSnetworx it seems correct but could it be a communication problem?
I uploaded plc, rsnetworx, panelview files in case someone could please help me find something wrong, thanking you very much in advance
Panelview 600 controlnet fixed
Hello i want to share with you how i checked this:
In the Node Adress of the Panelview Communication tab i was using 2 1 1:
2 Node of PLC
1 Backplane
1 Slot of Controlnet Scanner
the correct setup is 2 1 0:
2 Node of PLC
1 Backplane
0 Processor SLOT
i read the help and thought it was the Controlnet Scanner Slot and it was the Processor Slot, it is a Flexlogix PLC
Thanks Guys
Thank you for posting the followup !
As you have seen, CompactLogix and FlexLogix controllers have a 'virtual backplane' in which the controller itself is Slot 0.
Hi all, I have a Controllogix project, I added some DI/DO, AI/AO card online using unschedule connection.For DI/DO Comm Format: Rack...
6,192
Hey everyone, looking for advice in this particular scenario. Currently we have a controlnet bus that has (6) CN2DN devices and (2) powerflex...
228
Does anyone know of a cheap USB to ControlNet or USB to DeviceNet adapter (I'm looking for both). I thought PLC Cable would have one but I did not...
2,331
I'm having an issue trying to backup a ControlNet network. Within RSLogix5000, when I click on Module Properties of the 1756-CNB (Rev 5.001), the...
880
An issue occurred at an organization here in whereby the ControlNet card developed a fault. Card Details: Catalog/Series; 1756-CN2RXT B Part No...
452