I'm trying to read from a PLC5 controller that is separated by three DH+ networks from the ControlLogix controller that is reading the data. I'm having a little trouble configuring the path from the ControlLogix to the PLC5. Here is my layout:
ControlLogix Processor - Slot 0
DH+/RIO - Slot 1, Port A Configured for DH+ (Node 4)
}
PLC5 - DH+ Channel 1A (Node 1)
- DH+ Channel 2A (Node 1)
}
PLC5 - DH+ Channel 2A (Node 4)
- DH+ Channel 1A (Node 4)
}
PLC5 - DH+ Channel 1A (Node 1)
I have a message instruction set up in the ControlLogix using PLC5 Typed Read. My communication method is DH+ and the path is:
'DH_Plus' (configured name of DH+ port in I/O Configuration)
1 (Address of first PLC5)
2 (for Port 2A)
4 (Address of second PLC5)
2 (for Port 1A)
Destination node address is set to 1.
The MSG block just errors out with Error code 1 and Extended error 311 - "Port not available".
Can what I'm trying to do be done? Any help on how to configure the path would be most appreciated.
Thanks!
ControlLogix Processor - Slot 0
DH+/RIO - Slot 1, Port A Configured for DH+ (Node 4)
}
PLC5 - DH+ Channel 1A (Node 1)
- DH+ Channel 2A (Node 1)
}
PLC5 - DH+ Channel 2A (Node 4)
- DH+ Channel 1A (Node 4)
}
PLC5 - DH+ Channel 1A (Node 1)
I have a message instruction set up in the ControlLogix using PLC5 Typed Read. My communication method is DH+ and the path is:
'DH_Plus' (configured name of DH+ port in I/O Configuration)
1 (Address of first PLC5)
2 (for Port 2A)
4 (Address of second PLC5)
2 (for Port 1A)
Destination node address is set to 1.
The MSG block just errors out with Error code 1 and Extended error 311 - "Port not available".
Can what I'm trying to do be done? Any help on how to configure the path would be most appreciated.
Thanks!