I have a existing Panelview Plus 1000 that is communicating to a SLC 5/03 just fine. I want to communicate with at SLC 5/04 using the 1761-NET-AIC. I had problems in the past using this unit to read and write messages using Port 3 to Port 1. I was only able to start handshakes from port #1.
Will this be a problem when adding this PLC to my panelview plus communications?
See page 30 of the users manual
http://control.etfbl.net/real/AICmanual.pdf
Just did a project with the opposite; one micrologix and 2 panelview plus.
And yes, there were some problems!
The PLC had to be set to adress 1-31. So if the PLC was set to node 1 (in com port setup) node 0 and 2-31 are available.
My solution: first panelview ->node 0
second paleview -> node 2
And in the driver setup (both plc and panelview) max node adress must be 2
These were important settings, and was the ONLY thing that worked for me...
So it might be something you have to take into consideration when you will do this.
Hi I have a small dh485 network setup on my bench with 3 plc's. 1) ML1200 NODE 2, 2) SLC405 NODE 3, 3)SLC505 NODE 4 all connected to 2 AIC+...
1,734
Having a problem with communicating to older 5/02 1747 L524 plcs with the UIC interface. XP update happened to the laptop and the PIC was no...
2,710
Hello all, i have seen a few things here and there about connecting to a panelview 550, however i still would like to ask a few things, I have...
133
Hi all, I had a setup with 2 Micrologix 1100 connected to a Panelview C300 over DH-485. I was mandated to upgrade the HMI, and proposed to...
890
Hello, We have an older machine that has a standard PanelView (2711-T10C3) connected over DH485 to a SLC 5/04 PLC via a 1761-NET-AIC module in...
671