Im doing a project using RSView32... and a network of 5 SLC's all on DH485.
What I have done is run 2 of the SLC's off of the DF1 ports directly into the pc to save bandwidth.
I have 3 slc500's each giving about 300 tags each over the same DH485. Is this pushing what I can expect it to do?
Ive put all the tags in integers close to each other
ie N100:0-100 for bits
and im using n100:100/0 for bit level
Any comments?
Well, it depends on your polling rate... excluding packet header information and ACK/NAK responses, your basic data is:
3 SLC's * 100 Words * (16 Bits per Word + 4 Bits for Comms) = 6000 Bits total, so at 19200 Baud, you can probably handle that, polling at once per second. I don't know what the actual DH485 Protocol adds, but even figuring it doubles the required bandwidth, that's still only 12000 bps.
Considering messaging turn-around time though, you are probably just about at the limit for 1/sec polling.
Just a guess, of course.
thats cool, i could go out to 3000s without issue
I was thinking
if i set up 2 seperate topics per plc
have one at 1000ms for start/stops
have the other at 10s or even 30s for my trending and other stuff.
the trends go over 24hrs minimum fitted to the display.
Thanks for the answer!
Hello all, i have seen a few things here and there about connecting to a panelview 550, however i still would like to ask a few things, I have...
136
Hi all, I had a setup with 2 Micrologix 1100 connected to a Panelview C300 over DH-485. I was mandated to upgrade the HMI, and proposed to...
897
Hello, We have an older machine that has a standard PanelView (2711-T10C3) connected over DH485 to a SLC 5/04 PLC via a 1761-NET-AIC module in...
677
Hi, I have a SLC5/03 connected to a working HMI via RE232 port, and connected to a broken HMI via DH485 (RJ45), I want to use the cable that used...
3,320
Hey all, long time reader but first time poster here. I've been tasked with an odd one and was wondering if anyone else had experience in this...
17
5,354