disable DHCP server of Stratix 5700
Kataeb
Jan 2007
www.livelovelebanon.com
636
How can we disable the DHCP server on a Stratix 5700 ethernet switch?
It is running on a machine with Rockwell automation and drives.
We connected the G1 (or G2) port, with a fixed ip address, to the engineering office, for monitoring and support.
But the switch is acting as a DHCP server, providing ip addresses to the offices computers!
So, we need to remove all kinds of DHCP on the switch.
1783-BMS20CGN Stratix 5700
https://www.rockwellautomation.com/en-us/products/details.1783-BMS20CGN.html
Is this system configured to automatically assign IP addresses to replacement drives? If so, then you should not disable DHCP, if you want to retain this feature.
Plus, connecting automation equipment directly to business networks is usually a bad idea. Suggest you install a hardware firewall between the two networks.
If you need to disable the DHCP server function you will need the login and password for the switch and you need to know the IP address of the Stratix. Then you can use the internal web server, or if you are good at typing (unlike me) and are comfortable with command line interface, there is a way to do this but you need to consult the manual and access the switch with a terminal software using telnet.
Hey, I have 3 ArmorBlocks in my System. one worked fine.At the 2 others i can not disable the DHCP. I tried BootP an get Error 16, I tried...
1,970
I am using a 1747-AENTR on a machine rebuild. I can set the IP address without a problem using the AB BootP server. However, when I try to...
26
25,265
Hello, I am still new to PLC programming and I just got this job two year out of school so I don’t remember much. I was given a task were I have...
195
Hello. We have a Powerflex 700s phase II firmware 4.002, but the encoder card is burned. We want to disable it to use the Drive without motion...
471
As above. I've been fishing around on TIA portal but haven't found a "Disable channel" tickbox. Is there one? If so, where is it? Cheers
1,352