Download to a PV 900 w/ DH485 problem
tjoneill
Jul 2007
Michigan
66
Hello all,
I need some advice. I have a Panelview 900 #2711-T9A2 that I am trying to download to without any success. I tried using the 1747-pic driver with the Interface converter using the 1747-C10 cable and nothing. I even tried to get in by using the 1784kt driver with the PCMK card and the 1784-PCM4 cable and still nothing.
Can anyone help?
Thank you
Assuming that your PC properly supports the 1747-PIC/AIC+ driver in RSLinx, you might still not be able to connect to the PanelView.
Here's why: the 1747-PIC needs 24VDC power. That power can come from a controller's front port, or from a 1747-AIC isolator, or can pass through a PanelView terminal if the PanelView is also connected to one of those devices.
But if it's just the PanelView and the 1747-PIC, there's nothing to provide that 24VDC power. The -PIC and the PanelView are both considered "peripherals" on the DH485 network, to be provided with power by CPUs and network isolator boxes.
Next problem: It might be a typo, but you must be absolutely certain when defining a "KT" driver that you correctly specify the "PCMK" as the Device Type. Accidentally defining a -KT or -KTX on a laptop is an invitation to a Windows hardware driver conflict and operating system crash.
Frankly, I don't remember if the 1784-PCMK/PCM4 has the same requirement for the DH485 power pins. Be certain that you are choosing a node number for the driver that is different from the terminal.
I troubleshoot things like this by plugging the PanelView into an SLC-5/03 or 1747-AIC isolator and then attempting communications.
Don't forget that PanelView Standard terminals with v3.0 and later firmware can use ATA memory cards. Saves a lot of hassle with the old DH485 cabling.
Thanks Ken,
After I had submitted this problem, I tried again to connect to the PV through the PCMK card using the AB_KT-1,DH485 driver and it worked. I did nothing different...PanelBuilder was at node 0, Panelview was at node 2 and at the same Baud rate,, the only differnce i noticed is that i had deleated the other 2 drivers i had running in the background??
The problem that you were talking about with defining -KT or -KTX instead of a PCMK does exactly what you said it does, I found out the hard way a while back.
Thanks for the help again Ken
I have SLC 5/03 CPU and PV900 DH485 ; what method for uploading and downloading application into PV900 DH485? Thanks
4,555
Hello, i've been at this for months now, i tried creating accounts on the aveva website but it seems to never approve my accounts or at least when...
59
Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
111
Hi everyone, I got a Parker HMI, CTC PA2. I tried to download program to it but it froze in the process and could not finalize. Now, when I try to...
45
I am new In a CCW and as a beginner I am trying to learn programming but i am noticing that my CCW software is taking around 1 minute to download...
108