Downloading to a MicroLogix 1500
SSO
Jan 2008
Brockville
Hello All:
I have run into a peculiarity, or so I think, with the MicroLogix 1500. We use a data acquisition system that receives information on the status of the different equipment on the line from one main PLC. In our case the main PLC is a MicroLogix 1100. All other PLCs report their status to it via messaging, then on up to the acquisition system.
The problem arises when you want make changes to the MicroLogix 1500 logic (this model does not have on line editing). If the program that you are modifying in the 1500 was saved while the machine was in a running state, when you download some strange things happen.
We will make our changes and then download to the 1500 when the line is shutdown for break/lunch. The peculiarity we are seeing is: when you download to the 1500, the processor will want to be switched onto program mode, which is fine. When the download is finished you will see a dialog box stating the download is complete, do you want to go back to run mode. As soon as this box appears, the bits that were previously showing as off from the 1500 will now appear as on meaning that the machine the 1500 is controlling has come into running state, which should be impossible because the processor is in program mode. At this point we were monitoring the bits in question in the 1100 processor. As soon as you click on yes in the dialog box, then it shows that the 1500 controlled machine shuts down.
I know that the explanation is a bit confusing, but if you can get through it has anyone ever sent his before?
Thanks.
SSO said:
Hello All:
Thanks.
Sounds as to what you are describing are bits that are set in your offline copy. This is one feature with AB that can be annoying, when you download to the PLC all PLC rungs and file tables are copied. At least Siemens you have the option of logic files only to be downloaded.
CurlyandShemp has probably answered your question. I had a problem like yours but with a CompactLogix L32E. We had an issue that a certain conveyor would not home, but if you reloaded the program, it would home just fine. This was due to the bit being set high during programming. Drove me crazy for a couple of days, finally ended up being a prox switch.
Greetings All! We are looking for a simpler method of providing field techs with PLC updates (ML 1400, et al) and the means to download to a PLC...
2,442
Hi Guys When downloading a program using RSLogix 500. Is it possible to only download the program (ladder) instead of everything like all the...
7,462
Hi I've been programming in RSLogix 500 Micro Starter edition and its come time to download my program to my Micrologix 1200. I'm using a Win7...
13,606
I have a L82 system setup redundant that i need to download a lot of programs to in a critical environment. What is the process to do this and...
303
Hello everyone, I am trying to upload some parameters from a powerflex 523, and download them to a new powerflex 4. First problem is I’m not...
593