Fairly new to PLC programming so I have what is hopefully a simple question.
Should you/would you map raw encoder inputs to internal tags to use in your program as you would with digital/analogue signals? And if so/or not, why?
Thanks in advance,
LB
If by raw inputs you mean channel A and B or Pulse and direction wired into normal digital inputs, then you shouldn't do it because:
- It's going to be harder to code. You'll have to check for flanks to feed a counter, etc...
- You will limit the bandwidth of the encoder to the cycle time of the PLC, or you'll miss pulses.
- You may be able to program interrupts on the CPU, but that's not a nice approach on PLC's, considering that there is dedicated hardware for it.
So the best way is really to use a counter card and interface it with the standard way for whatever brand of CPU you have.
This
If I am correct assuming your meaning, it's handy to be able to see the pulses for troubleshooting purposes. As for control, the inputs typically are too well filtered to be useful in moderate speed applications. But for troubleshooting, being able to see the inputs without having to get out a voltmeter and opening the cabinet can be useful.
Yes, my apologies, I meant Channel A & B inputs. I am using a CompactLogix L30ER CPU and I have a High Speed Counter card so I will use the inputs directly from the card in my program. Thanks for the responses!
With CompactLogix HSC cards, tags are automatically made that show the status of the channels. For example, Local:X:I.InputStateA0 will show the status of A0.
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
301
I have an application using an incremental encoder and then I convert it to degree (0-360) using calculation program. For a while, the calculation...
365
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
18
1,077
Dears, i am trying to change the series of encoder from A to B, but the program do not has this option (Rslogix5000, 20.06 the old encoder was...
220
Hi all, I am working with an incremental encoder (ABZ signals, 360 ppr (so 1440 counts per rev)) to replace the existing "manual" encoder wheel I...
51
2,715