ethernet communication to motoman robot

ddwilson1

Member
Join Date
Apr 2006
Location
Indiana
Posts
10
I am using rslogix 5000 with micrologix L32E processor and point io. everything except the robot will communicate and is working fine except the robot that conection is giving me a code 16 #0204 connection request error. I can ping the IP address for it with no lost packets but always get the yellow triangle in RSlogix.
Any suggestions?
Doug
 
16#0204 is an ordinary timeout; the 1769-L32E cannot reach the Motoman device over Ethernet.

Check to be certain the subnets and subnet masks are correct for both the CompactLogix and Motoman, and assure that PING test by unplugging the Motoman and pinging again to be certain you don't have an IP address duplication.

How did you define the Motoman I/O connection in the CompactLogix ?
 

Similar Topics

I'm retrofitting equipment, but I didn't want to change the electrical characteristics of the panel. In this equipment I have a dedicated...
Replies
0
Views
72
I have a contractor at my water plant installing 3 brand new Powerflex 7000 VFD's for my High Service pumps. I would like to control these via...
Replies
6
Views
1,011
Hi All, We are planning Establish communication between Power Energy Meter (Schneider PM5320) with Rockwell PLC. I am unable to get the Assembly...
Replies
4
Views
763
Hi All ... In one full plant, all machines are connected to networks. above 500 ip address... that consists of plc,servo,hmi and third party...
Replies
3
Views
1,554
Hi All, I have a requirement of communicating my 5380 CPU with Zebra ZT411 Printer. Is there any one who did this before ? Do we need to have...
Replies
2
Views
928
Back
Top Bottom