You have all kinds of interesting stuff on this network. Acromag, Moxa, ProLinx, A-B... There's a switch with a webpage interface that I can see, with a Java applet showing you statistics.

I see Acromag devices on subnet 192.168.144.x at IP addresses .81,82,83,84,94,95,96,98,99,101, and 102. Did I miss any ?

The first capture shows traffic mostly between .31 (the 1756-ENBT) and .81 (one of the Acromag units).

The second capture shows mostly the data originating from the 1756-ENBT to many nodes but not the reply data and the data replies are mostly not being seen. This might have been taken from an incorrectly configured mirror port or a switch.
 
Yep. Moxa switch uses a Java interface to get show stats.
The first capture shows traffic on a unit that I've had fault quite a bit, but I didn't see anything out of the ordinary.

The second unit I had the mirror port set incorrectly, or there is never any data coming back. I'll grab a hub & do it the simplest way possible.

Was there anything that you saw that stood out?
 
Open up the Traffic2 file in the first capture you posted and look at the traffic around Frame 458.

Ordinarily there's one packet from the -ENBT at address .31, and another packet from the Acromag at address .81.

Around Frame 458, each device starts to have to retry once, because it didn't hear a corresponding packet from the other device. The retries are 50 ms apart and usually there's only one retry.

I think that this indicates that somewhere in the lower level of the network there is something keeping packets from being correctly transported from .31 to .81 and vice versa. It might be a loose plug, or a bottleneck in a switch... it's hard to say.

When a device retries, it increments the sequence number. If the other device doesn't retry, you get a difference in sequence numbers. If both devices retry the same number of times, the sequence numbers also don't get out of step.

You can see in that capture file that the sequence numbers of adjacent packets are out of step; by the time you get to Frame 1000 of this capture, the values are 961531 from .31 and 956395 from .81.

This means that the 1756-ENBT at .31 has retried about 5100 times more than the Acromag has. I think this means that the Acromag is more often not replying (or the reply is not being heard) than vice versa.

Disconnect the Acromag and the sequence numbers will go to zero. That will let you establish what the average unbalanced retry rate is over a period of time.
 
With more Ethereal Traces, I think I got to the bottom of this.

I had a device (Moxa EDS-308 Switch) Querying on IGMP. It was flooding the Network with Broadcasts, so I turned the Querier off. I beleive this is it, when I'm sure, I'll hit it back.
 
Just wanted to say thanks for the excellent lesson Ken. I have played with Ethereal and have used it to poke around a network, but I think this thread has given me a firmer grasp on what exactly I should be looking for
 
CroCop said:
Doesn't look like that did it.
Hmmmmm.
Going to try to run a few more traps in the morning......

Turns out "this morning" turned into "this afternoon". Funny how that happens.......

Anyhow,

I've had a major fault, and the ip addys in question are .31 & .111.

They are both Rockwell Devices, a 1756-ENBT & a 22-COMM-E. I can ping both, I can see both on the network using Look@Lan.

Problem is, the 2 devices don't see eachother.

I've attached a Ethereal Trace, one from the Controller Side, the other from the IO Side. Put ip.src == 192.168.144.111 or ip.dst == 192.168.144.111 in the Filter, Click Apply, & see what's going on.

I'd sure like it if Ken saw this & weighed in.:geek:
 
Also,

If I reset the Main Switch I'm using, it will work properly. Also if I disable/enable IGMP Snooping on the Switch.
 

Similar Topics

Hello all! I have some machines that run an SLC 5/03 and occasionally a fault is generated. Recent Example: A power supply wasn't screwed in...
Replies
3
Views
428
rslogic 5000: I need to setup a alarm to detect if Ethernet has lost connection I have searched everywhere on the net and can not find out how to...
Replies
2
Views
3,901
Hi all, My ethernet port on my laptop recently broke and I was hoping to just use a usb-c dongle in the mean time to go live on my PLC until I...
Replies
14
Views
472
Hello, I've been trying to learn this a while now and still have not found out how this works. I have an Omron CJ2M PLC and an ABB ACS 355 VFD...
Replies
1
Views
266
I have a running backup of Citect and plc and I want to make a spare PC station so I have installed the win XP and somatic net v6.0 and import the...
Replies
3
Views
136
Back
Top Bottom