Expansion and/or DeviceNet I/O update times on a SLC
robertmee
Feb 2008
NC
2,030
Question:
I have a 100ms (duration) pulse that I need to sense in a SLC 5/04. It is currently running 20ms scan times so on local hardware Inputs wouldn't be a problem. However, the 10 slot rack is full of all AC I/O modules (with the exception of one DN Scanner) and I need to sense these 100ms pulses (8 of them) from a solid state DC source.
Options: Add flex I/O vis DN or add an expansion rack. My concern is how are DN or Expansion I/O updates handled?
Expansion: I would assume (maybe incorrectly) that since it is a hard bus connection from Rack to Rack, the I/O is handled the same as if it were on a local rack. If so, that would probably be the safest bet.
DeviceNet: Does the Adapter/Scanner combo buffer the I/O? Or do I have to add the overhead of getting the I/O to the SLC image table to the overall update time? I don't care if the pulse is delayed by Xms, but I do care that it remains 100ms in duration. Well, not even a perfect 100ms, but a duration such that I would NEVER miss a pulse due to scan/update.
since the CPU scan time is already 20ms (and probably not going to change much) the local I/O is not important. the question is what do you have on devicenet?
also since we are talking of only 8 DC inputs (sensors?) you could use pulse stretching inline adapters. some of them are DIN-rail mounted (like baluff BES 516-IV 2) while others are simply inserted between sensor and cable (or replace cable).
I'm in the preliminary discovery stage right now and all I have from the customer is the RSS program. I don't have the DN file so I don't know. But judging from the PLC code, it looks to be about 168 words of DN info coming in.
The safe bet is to use an expansion chassis. All SLC-5/0x controllers will control up to 30 slots in up to 3 chassis connected with backplane extension cables. As you add slots to the SLC backplane, the I/O scan time goes up a little, but it's generally negligible (in the 1-2 ms range). Expanded chassis are addressed and scanned exactly the same as the chassis that holds the controller.
On DeviceNet, the variables of uncertainty increase. The 1747-SDN's first 32 words are part of the normal I/O scan, but any words in the "M-files" are copied using logic to the SLC data table and take a little time. The 1747-SDN scan is asynchronous to the SLC scan, so you end up doing little "worst-case" calculations when you get into the 1 or 2 scantime domain.
Unless your DNet is extremely busy, I doubt you could miss a 100 millisecond input pulse.
I'd go with an expansion chassis, but also take the time to examine the DeviceNet configuration to see if you can optimize it. I just optimized a DeviceNet that was taking 50 milliseconds to scan down to about 10, using change-of-state connections and stablizing the signal so the network could handle 500 kb/s.
Great Info Ken! Thanks!!
Hi First post here! I admit I am not too used to handle interrupt OBs in Siemens. I have a customer who has been buying a standardized solution...
256
Good morning Guys, PLC: micrologic 1500 LRP 24bwa c series soft: Rslogix 500 We are required to consider the weight of the product in such a way...
1,405
I am using a M221 PLC (TM221CE24R) which provides me 1 Rs485 port, which I am already using to communicate with a sensor (Rs485/Modbus). My...
755
We have an AB PLC that has a faulty expansion cable between Bank 1 and Bank 2. Part # 1769-CRR3. I found a small burn mark on the board. Being...
770
I have used the 1769-CRLx to expand the size of an L33ER CompactLogix PLC to include additional modules in the local rack. Is this also possible...
2,015