Experts on Schneider Electric TM2AMM6HT!
dwpang
Aug 2012
singapore
68
Hi guys, i am doing a project on analog signals and will like to ask about characteristics of TM2AMM6HT analog modules.
For the project, i going to use a flowmeter capable of giving 4-20 mA active signal to the module, and would like to know if it can work with the module or cause any damage to it.
Attached is a layout of the supposed connection from the flowmeter display to the module itself.
I fear that the 24VDC in the signal will damage the analog module.
If it does not work, anyone knows of any Schneider Electric analog modules capable of running on such active signal?
Can't change the flowmeter active signal to others as I have already bought it.
Thanks.
Actual voltage from the FM will be whatever is required to push through the AI internal shunt resistance. Typically 250Ω, so 5V @ 20mA... No different from a passive device, except the Vs is internal to the instrument.
hi lemming thx. yup indeed the tm2amm6ht input impedance for 4-20 mA is less than 250 ohm, so only can give abt 5 volt at most.
shldnt be a problem then! will test and see!
I'm trying for the first time to use this HMS-EN2SE-R to communicate very tiny ASCII comms (3 characters max) From a Logix L71 to a very dumb...
399
I'm trying to set up a Yaskawa GA500 inverter to do multi- speed stage start up. I only want 3 stages. On run, ramp to 15HZ, wait n seconds to...
1,747
Just wanted to see if there's any recommended resources for motion control education. I have an application I'm working on with a linear motor...
2,743
A customer of mine has a problem. His AB PLC5 1785-L40E is faulted, and the plant is at standstill. He cannot get online to diagnose the fault...
19
3,526
DCP – Discovery and Configuration Protocol packets are well documented, except one field "Xid". This is a 32 bit value, it looks like it has...
1,489