Guys,
I have an application using FactoryTalk ME version 7.
The application has been running fine for a few weeks now. I made a change today and downloaded the new application.
All of a sudden most of my analogue tags are showing ***, and I am also missing some digital tags.
All of my tags are created in a tag database, so I am not pointing directly at the PLC.
If I go into the tag database, and redo the tag, I get the analogue value back.
This also works when I hit the test button. That is the value of an analogue tag is showing **** redo the tag and hey presto, press test and my analogue value is back.
I have got hundreds of tags that are missing, and was wondering if anyone had seen this before?
Cheers
Mark
Not seen it before, but if I were you, my first move would be:
- Export all tags to CSV
- Open CSV and compare a working tag to a non-working tag
- If there are any differences at all, correct them
- If not (or once differences are corrected), delete all your tags from ME and re-import your CSV
I don't have to remind you to back everything up first, of course? ;)
When you downkloaded, did you check the "replace communications" checkbox? Is it possible that your device shortcut for the design and runtime target changed?I've seen this before and it has caused issues as you described.
Thanks for the replies.
I have exported the database to a .csv file and I can see no differences there.
After a little bit more investigation, I don't know if I have stumbled across the problem or if it is just coincidence.
For example, a tag that is working looks like this
Tag database: Instruments\LT5103_Percent, looking at PLC tag [PLC101]LT5103.Scaled_Percent
Tag not working looks like this
Tag database: Instruments\LT5103, looking at PLC tag [PLC101]LT5103.Scaled_EGU.
Now when I add these tags to the display properties, under the connections tab, I get this.
{Instruments\LT5103_Percent}
Instruments\LT5103
Notice the parenthesis that are missing on the tag that won't work.
I have tried adding the parenthesis manually but factorytalk removes them.
The tags are now working when I press the test button, but still won't work when I download to the terminal.
AAAAAAARRRRGGGGGHHHHHHH!!!!!!!!!!
Cheers
Mark
If they're working on test mode, but not when downloaded to the screen, I'd double check all of your communications setup. Make sure you've copied the RSLinx Enterprise design path to the runtime path, and make sure that when you download you replace the communications path. Also check your data formats on the tags, make sure you haven't got an analog tag configured as digital, etc etc.
Did you try importing your CSV back in?
For some reason that I do not understand, FactoryTalk is showing the Day of Week in the time and date display, despite the fact that this isn't an...
1,232
Hi all hoping someone here may have ran into what im having, tech support is not being particularly useful, had someone teamviewer in then go...
2,006
Just a little bit of a query. When I am in the office and not connected to the automation network, I cannot seem to see any AOI tags in the...
1,197
Hello I have an emulator SoftLogix on VM1 and running FTView ME on VM2. I am trying to link the two by setting up a short cut inside FTView but...
2,156
Hello, I'm having a problem since yesterday, can't figure out why. All new plc tags (either controller type or program) won't show in...
6,592