I have a peculiar problem. I have a Compact Logix PLC, which is hooked to another device. I have a PERIODIC routine, which cycles at every 213ms and reads a bit from this device. If this bit is HIGH, its a fault and it should show up on the ALARM panel.
I have other Digital I/O which do show up as faults when they are HIGH, in the ALARM window, but they are part of the MAIN Program [Continuous task].
How do I set the ALARM list in the PanelView touchpanel to display this fault, which happens in the periodic routine.
Thanks,
Sunnyvaleplc
The only way is to latch the alarm auxiliary bit, no matter how fast the alarm takes place it will stay on. That´s the way I do it, maybe some else has a better idea. You can unlatch this bit when you acknowledge it.
I would agree with having the alarm latch or hold state. You can check the alarm settings as well. There are settings for how long the alarm has to hold for it to show up. I think the min is 50msec, you could try that. There is also an update or refresh time that you could change. But, latching in the PLC is to me the best way to do it.
Thanks a lot for suggestions both of you. I will try the latching and unlatching inside the PLC. if there is a FAULT, then I will latch it, start a timer for 100ms and when the timer expires, I will unlatch it. This should allow enough time for the alarm window to update.
Thanks,
sunnyvaleplc
I'm working on troubleshooting a PLC for a piece of manufacturing equipment. The issue I'm trying to resolve is an open wire fault not getting...
546
Hi guys, i am facing problem on pilz (type pnozm1p.this problem is ofault led is continue flashing.we made several time power reset but still...
5,167
Hello - I need to show PLC5 card status (comms, fault, etc.) in RSView32 and am not sure where to start. Any help would be greatly appreciated...
6,719
Hello everyone, We have a AB 1756 L55m13 controller and profibus adapter sst-pfb-clx. The adapter is connected to six Vfds (all Siemenes...
2,661
HI there. i am in urgent need for help. i have SLC5/03 CPU with some I/Os.Fault LED is continously blinking and PLC is not going in run mode. I...
4,903