Flashing a PLC

Psapkota

Member
Join Date
Jan 2021
Location
Texas
Posts
8
Hello all!
I have a 5069 -L310ers2 plc that has A1 and A2 Ethernet port.
I connected to A1 port while flashing the plc and it was successful.
The plan is to have plant network on A1 and controls network on A2.
I have my all Ethernet devices such as Aent and vfd on A2.
But when I connect From A2 to switch, I cannot go online with the plc but when I connect from A1 to switch, I can go online. But none of my Ethernet devices come online on that time.
What could be the reason?
Does it even matter if we flash plc from A1 or A2 port?
Thank you
 
When you're connected via USB, change port A1 setting to Dhcp and apply. Then change port A2 setting to static with the IP for your machine network.
 
Last edited:
How have you configured the Ethernet ports, have you configured the ports as dual ip or single ip?
I didn’t change settings on that one… I checked the properties of A1 and A2 and it says A1/A2 Dual-IP for both A1 and A2 Ethernet.
Do I still need to configure the ports?
 
Last edited:
You can flash from any of the ports (A1, A2, USB). Chapter 9 of the manual covers this in detail:


Are you in Dual IP mode? Do you have a diagram of the network in question you can share?
I don’t have the diagram as of now…the diagram just shows A1 to customer network and A2 to controls….
But I don’t have to connect to customer network now…And I think I am in dual mode… as it shows A1/A2 dual mode on properties
 

Similar Topics

Hi All, I am new here , I am trying to flash AB plc 5380 safety guard logix Freeware 32.012 which is our program and old plc, but It does accept...
Replies
11
Views
418
Hello everyone, I am having issues with an output module connected to my 5069-L306ER PLC. The modules I have connected are a 5069-IA16 in slot 1...
Replies
1
Views
706
If I have some LED andon lights that are steady is it normally ok to use PLC logic to flash them? It's a red light that needs to be solid when...
Replies
5
Views
3,348
Hi! I need one bit flashing on a PLC5 (AB)... For a SLC500 I used a system file bit that make it but for PLC5 I can't found anyone... I would...
Replies
6
Views
6,205
I have a slot PLC that has all lights on solid and the WinLC/WinAC display all the lights are flashing. It will not let you restore the project...
Replies
0
Views
3,683
Back
Top Bottom