Hi!
I need one bit flashing on a PLC5 (AB)...
For a SLC500 I used a system file bit that make it but for PLC5 I can't found anyone...
I would like to know if there is some bit that makes it or if there is another way to do that on PLC5
Thanks!
So there's no system file bit for that like in SLC500?
Okey I will try this...
I though something similar but I hate using timers!
Thanks anyway!! 🍻
S:23/0 will give you a 1 sec pulse
S:23/1 will give you a 2 sec pulse
And so on and so forth no need for a timer unless you need a specific interval less then one second or you need to synchronize it with some other function.
That was exactly what I was looking for! Thanks!
You can also create your own free running timer in a PLC/5 that is similar to the SLC500 S4 file.
Create a self resetting free runnig timer with a large EVEN numbered preset.
XIC T4:0/DN TON T4:0 .01 32760 0
Use bit T4:0/ACC/0, T4:0.ACC/1 T4:0.ACC/2, T4:0.ACC/3, etc for a clock pulse with a duty cycle of .02, .04, .08, .16, etc.
I have 6 powerflex drives, two encoders and one 1734-ADN point IO rack on devicenet network connected to controllogix processor. There are 60...
3,359
Hi... I'm still learning how to code for PLC's Using Allen Bradley SLC 500 and RSLogix, I made a flashing bit using timers. Now, I assumed if I...
2,026
I have a 1769-L24ER-BB1B and I am trying to flash it to 34xx, its flashing red and faulted, when I try to flash it I get a popup stating it needs...
287
Hi Guys, I have a 1769-L24-QBFCB1 that has the OK light flashing on the embedded counter module. The manual states it is a resettable fault, but...
127
Hello all. I have a remote that uses a 1734-AENTR series C. We had to change it to a new one and, after adjusting the IP and number of slots...
596