Flex IO module reading wrong
CQ21
Apr 2021
Columbia
61
Hi all,
I have a 1794-IT8 module that doesn't seem to be reading the correct values. I have set it up correctly for the appropriate type of thermocouple. I have attached a screenshot of my read words 9 and 10 as well as the write words.
Read 9 = N11:39
Read 10 = N11:40
Write 0 = N11:41...etc
I have configured all channels for type J thermocouple and I'm only using the first 4 channels currently. I've also attached the integer file in decimal for reference. The only thing I've noticed is that bit 7 in read word 10 is true when it should be false by default. Could it just be a dud module? I did buy from ebay...
Or are you saying the whole card is not working?
swap channels with a known good channel?
Get a heat gun and heat one of the Thermocouples up see if you see any changes on the input words?
I recently came across the 20-HIM-A6 device (20him-um001_-en-p.pdf) being used to copy parameters from one 525 drive to another. However, upon...
782
I've been talking with PowerFlex 525 Drives using the Comm C module with a non rockwell controller without any issues. I went ahead and loaded...
1,032
Hi All, We are trying to commissioning Power flex 755 embedded(EENET) with Port 8 115V IO module mounted. It is communicating but IO module...
1,141
Hi everyone, I have this issue with a PowerFlex 755 that it mount a Safe Speed Monitor option module. Frequently, while running, appear the error...
2,366
Good afternoon folks, We have twin PowerFlex 755 480V, 14A AC drives (v14.005 fw) with embedded Ethernet that perform the same function side by...
2,517