FLEX IO with ControlLogix via EtherNet/IP
Oct 2010
Chicago
19
Hi guys! I have problem with communication between
Logix 5561 and Flex 1794AENT.
I have Logix 5561 connected to EtherNet/IP network, via two modules:
1. 1756-ENBT - talking with PanelView 1250
2. 1756-EN2T - talking with 7 remote 1756-ENBT(5 chassis(13 slots each))
I have to add 8x1794-AENT, and in future five more PanelView's
I tried to add 1794-AENT same way like 1756-ENBT, but no any luck.
Can I talk with 8x1794-AENT via 1756-EN2T(already working with 7 remote racks)?
How to setup communication with 1794- AENT in RSLogix 5000?
Can I talk with five PanelViews via one 1756-ENBT?
What do you mean "Add the 1756-ENBT" ? You don't add that to the EN2T. It is a separate Ethernet module.
Drop it in the rack, give it a name, go to the "Ethernet" network under the module, right click, "New Module", "Communications, 1794-AENT".
If that doesn't work, you need to tell some basics, like, oh, say, what rev of firmware for the CPU and the modules you are adding.
I tried to add 1794-AENT same way like 1756-ENBT, but no any luck....
You cannot add Flex I/O online
Yes
It just works when you add the modules - just as if it was 1756 I/O
Yes
You might need to configure such a large amount of remote IO as "Rack Optimisation"
Something i ran into that has me stumped, hopefully someone can explain. I have powerflex 70's connected to a L7 cpu using a 1788-en2dn. The...
1,361
Customer installed two SMC Flex soft starters to replace Dialog Plus units that died. They have everything set up correctly on one of them and...
4,972
Hi Everyone, Would like to ask about something we encountered on our work and would like some advise. We are upgrading a SLC controller to a...
2,469
Hey All, I'm currently building a control system for a large building in a industrial setting. Doing lighting, vent, roof control, door access...
3,499
I everyone someone can help me, I have a problem there's a fault in comunication, a controllogix lost conection with the RIo, RIO 0, RIO 1, RIO...
3,358