GE ENET station manager

jjack230

Member
Join Date
Aug 2017
Location
Brisbane
Posts
5
Hi
I am just starting out at a new job full of GE systems.

I have a IC695ETM001 ethernet card which has a RS232 port for Station manager access.

I can currently see some info (such as IP, firmware version etc.) from the card when I connect with Putty and cycle the power but I cannot send commands to the card. I've tried Putty, hyper-terminal and a standalone Station manager terminal from GE but nothing works.

Anyone know whether I'm missing something?
 
I'm wanting to do some monitoring on that card. We've put in a replacement time and time again. Every card that goes in has the "Log Empty" indicator light turn off after 30 seconds. So I want to view that log.
 
I found the issue.

Turns out that you need the serial cable provided by GE.

You can't just use a standard cable. Haven't checked the wiring configuration but theres something different.
 

Similar Topics

Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
Replies
0
Views
61
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
169
Hi, I am looking to migrate some of our Electronic Overloads off of a Troublesome Devicenet Segment. Is there any documentation confirming the...
Replies
5
Views
143
We've run into an old system that we are upgrading which is still running Steeplechase with Citect using Devicenet to Wago. I had some experience...
Replies
4
Views
165
Sigh, DeviceNet noob... I have a 1756-L55, with a DeviceNet module, and 10 PF700 all commanded with DeviceNet. One of the PF700's blew up...
Replies
3
Views
151
Back
Top Bottom