Getting 5/04 corrupted processor error
rakesh.tqm
Oct 2015
Chittoor
Hi, we are using 5/04 processor and when we are going online it is showing the processor is communicated in RS Linx. When i select the processor and trying to go online or upload or download the program, it is showing as corrupted processor or processor failed error. Am using serial port for the communication.
I tried with 5/03 processor and it is working fine.
What would be the possible causes.
Most likely is that your 5/04 processor is firmware 10 or better and you are trying to connect to it with older RSLogix 500 software.
Hi and welcome to the Forum!
I think this is what KuulKuum is referring to?...
36596 - Error: Corrupted Processor or No response from processor at selected path/node!
Access Level: TechConnect
Regards,
George
Ok, I have a bit more time now...
For those without TechConnect (Mickey, I have you to blame for all this "extra" work!)...
RSLogix 500 v7.10 introduced support for the selection of "FRN 10 and later" SLC processors under "Processor Type".
Versions of RSLogix 500, prior to v7.10, cannot go online or upload/download to FRN 10 or later processors, if they contain a program that was configured for an "...FRN 10 and later" Processor Type.
So what can you do?...
1) The simplest thing to do is to upgrade RSLogix 500 to v7.10 or newer.
Or...
2) You could access the controller with a compatible version of RSLogix 500 (from another source) and edit the Processor Type from "...FRN 10 and later" to "...FRN 3-8". Even though this is not the correct selection for this processor, the program will download. This will then allow pre v7.10 software to interact with FRN 10 or later processors.
So will it be door number 1 or 2?
Regards,
George
Hi how's it going. Was just wondering if someone could help me out. Recently one of the guys over on the LinuxCNC forums put me onto getting an...
354
The application was working in Twincat 4022.16 Used VM for offline. recently changed the laptop and the getting the error with Message as below...
84
We are using wincc scada WinCC system software V7.5 SP2 , connected to few plc . Past 3 weeks we getting this alarm continously when we checked...
115
I am very, very new to PLCs. I only have experience with Picos, but I knew enough to save this from the dumpster. Apparently, everything on it is...
711
Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
18
1,533