Getting timer value from HMI to PLC

Directorone

Member
Join Date
Jun 2011
Location
Los Angeles
Posts
5
Hello All,

I am fairly new to the Mitsubishi software and I ran through the tutorial and pretty much have my entire program written except for one part. I have an FX3U-32MR/DS and I am trying to get a value from my GT1055 for the timer and another for the counter. Can someone point me in the right direction for this?

I don't know if this is correct, but I have one text field on my HMI addressed DO and another D1 so for timer 1 I put T1 D0 and timer 2 I put T2 D1. All help is greatly appreciated.
 
Yes this is correct but remember that D0-255 are not retentative by default 255-512 are or you can set the range in GX developer to what you want, remember that the timer is 100ms so typing in 10 will give you 1 second but on some HMI's you can scale the value so entering 1 multiplies it by 10 then downloads it to the plc
 

Similar Topics

The application was working in Twincat 4022.16 Used VM for offline. recently changed the laptop and the getting the error with Message as below...
Replies
0
Views
66
We are using wincc scada WinCC system software V7.5 SP2 , connected to few plc . Past 3 weeks we getting this alarm continously when we checked...
Replies
0
Views
95
I am very, very new to PLCs. I only have experience with Picos, but I knew enough to save this from the dumpster. Apparently, everything on it is...
Replies
13
Views
633
Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
Replies
18
Views
1,482
Good morning guys; Im new at AB plc, and i just need help about a table or a list called something like "exchange data table" in French it is...
Replies
4
Views
787
Back
Top Bottom