Hello, hoping to get some feedback on this overnight.
I have a couple of Omron FQ2 cameras connected to a 1763-BBB Micrologix & 1762-OB8 transistor output module that have been added as an independent system to an injection molding machine. We have had IO fail on the camera and trying to determine where a possible cause may be.
We had not directly grounded/earthed the 0V/-. But during some testing we found that the 0V is tied to earth. We traced this to an internal link on the 1763-BBB Micrologix between its earth terminal and the 0V/-. Unless we don't earth the controller I think we should be looking to formally ground the 0V at the common 0V terminal block. Other devices associated with the system have ether no connection between their 0V terminal and earth or some lowish resistance or assume capacitor connection to earth (resistance changes when metered).
My question is why would we not want to earth the 0V. It would seem unlikely at this stage that we can fully isolate it anyway.
Thanks in advance.
Lots of commentary:
URLs to discussions of grounding the power supply
Control.com: PLC auxiliary power supply - floating or grounded
http://www.control.com/thread/1236976011
PLCs.net: 24 Volt Inputs and Grounds (2004)
http://www.plctalk.net/qanda/showthread.php?t=13249
PLCs.net 24v power supply (2012)
http://199.193.246.108/qanda/showthread.php?t=73352
PLCs.net: Grounding question 24v power supply
http://www.plctalk.net/qanda/showthread.php?t=30839
Mr.PLC: Ground the 24VDC Power Supply Common?
http://forums.mrplc.com/index.php?showtopic=15175
I trust that you have found the little metal plate on the backside of the ML1100 connecting it to the din rail?
You have to take that off as well as disconnect the ground terminal if you wish not to have the controller grounded.
This has caused me problems in the past as the short between 0V and ground will sometimes show as a fault on some fault current devices on ships.
Can someone help me on grounding 24vdc power. Some do and some don't, some say you should and some say shouldn't ground to an A/C ground. :confused:
16,609
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
275
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
439
Hi, Our customer has bought a machine a CNC wood cutting machine. It states that it need a seperate 16mm2 EMV"ground" in addition to our 5G16mm2...
606
I have a Beckhoff PLC with many AI modules. Most devices are loop powered using the same +24 VDC power as the Beckhoff Bus Coupler and all is...
672