Could l suggest, read the regulations, install to it, hah prestoo no issuie

The NEC code book is hard to interpret for someone who has not been taught the code such as in an electrical apprentice's course. This is a question of wiring practices more than a controls question. I am a Master Electrician and what I stated earlier is true both control cabinets should already be bonded to the grounding system via there equipment grounds that are run with the feeder circuit. Provided it was installed correctly. If one of the cabinets were installed without an equipment ground and you run a ground wire between the two cabinets, and one of the power conductors short to the cabinet without an equipment ground then all that fault current will take the path of the small ground wire between the two cabinets. This fault current can become very large very fast and melt down the ground wire. So I guess in a nutshell, check that both cabinets have an equipment grounding conductor from the feeder circuit bonded to them and you are covered. No need to pull a ground between the two cabinets.
 
As a few have pointed out, the cabinet supplies should aready have a earthing conductor.
The OP's 'link' between the 2 cabinets is comms & 24vdc.
IMHO, there is no need to run a 'grounding' conductor... If one is run, then I think it is a 'bonding' conductor, again IMHO
 

Similar Topics

Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
Replies
5
Views
306
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
Replies
9
Views
449
Hi, Our customer has bought a machine a CNC wood cutting machine. It states that it need a seperate 16mm2 EMV"ground" in addition to our 5G16mm2...
Replies
2
Views
610
I have a Beckhoff PLC with many AI modules. Most devices are loop powered using the same +24 VDC power as the Beckhoff Bus Coupler and all is...
Replies
5
Views
680
I was once asked a question in a job interview. "Do you ground both ends of a shield?" I answered: "You only ground one end". Apparently that was...
Replies
12
Views
4,990
Back
Top Bottom