++However if I just hook the 24VDC OUT to the brown wire and put the blue on the input, won't I also have to attach the input to the common also or is this done internally? Am I just way off base here?++
The COM terminal on your PLC must be connected to your -24VDC (or DC COMMON) point. Otherwise, the circuit is not complete and none of your inputs will ever work.
Think of a 2-wire sensor as a 3-wire one, with the black wire removed and the blue one used in its stead. Disregarding all that was said above regarding the LED indicator, it is just a normally open contact... Or, if you consider the LED, it is just a diode in series with an N.O. contact, that can be turned on or off...
The COM terminal on your PLC must be connected to your -24VDC (or DC COMMON) point. Otherwise, the circuit is not complete and none of your inputs will ever work.
Think of a 2-wire sensor as a 3-wire one, with the black wire removed and the blue one used in its stead. Disregarding all that was said above regarding the LED indicator, it is just a normally open contact... Or, if you consider the LED, it is just a diode in series with an N.O. contact, that can be turned on or off...