Hmi issues- only alarms appear, no warnings
joerack
Feb 2022
italy
I'm using tia portal v16 with physical plc 1211c and simulated Hmi TP700 comfort.
plc and hmi are connected correctly.
I have 2 arrays of 32bits one for alarms and 1 for warnings, while hmi reads 4 words each. All alarms are displayed at the right moment
My issue is with the warnings=> My "turn on power" should appear as a msg (no ack) warning to turn the power on.
Nothing appears tho. I've tried everything. Warning is configured correctly as class and is enabled in hmi alm. box, double checked from plc DB the correct bit is up
What else should i do? Thx
In the HMI Alarms list, the text (in the displayed language!) is correct, the alarm class, trigger tag, trigger bit, trigger address are all correct?
In the alarm view on the alarm screen, under general, display, alarm class, enable, the warning checkbox is checked?
If all of this seems ok, make an indicator (whatever kind doesn't matter) on a screen and tie it to the warning trigger bit and see if the HMI is actually seeing this bit turn on.
I've solved it. if plc declares bools, hmi can read alarms as words no problem.
But messages must be declared as words from plc or hmi will not read
Hi I have a couple of hmi panel view plus 700 Hmi and we keep dropping coms /stars in the data boxes I’ve checked the plc and unmanaged switch...
178
Hi all, long time lurker and finally decided to sign on to get some help for those smarter and more experienced than I! I'll put it out there...
1,282
Hi All, At site, there is a Pro-Face 19” screen Model: SP-5800WP FWXGA complete with PFXSP5B10 box. Connected via Ethernet to the screen...
3,140
Hello, I have been using TIA Portal V16 on a project (S7-1500) and when I am online to the PLC (all devices, FB's, FC' DB's etc. are green)...
11,010
Hello all, I'm new to the Sysmac Studio software and I'm having an issue with the HMI screens crashing. I have a screen that shows the active...
1,974