How high, high speed input required?
I believe there is only one HSC on the ML1100. It can be assigned to one of the four high speed inputs.
You are not the first programmer to be confused by this.
I have not used one of those units, I am just repeating what I have read in earlier posts on this subject.
There are a bunch of LONG discussions at MrPLC.com. (Search "HSC 1100".) In those threads there are methods described that allow you to use more than one of the high speed inputs by using input driven interrupts instead of the HSC.
Here's one of them:
http://forums.mrplc.com/index.php?showtopic=6520&hl=
Hope this helps...
Paul
The confusion seems to be the difference between high-speed Inputs and high-speed Counters.
On the MicroLogix 1100 and 1200, Inputs 0,1,2,3 are wired into a faster input circuit than the other Inputs on the controller.
Those inputs can be configured and used as pulse catching (latching) inputs, as high-speed interrupts, as inputs for the Programmable Limit Switch (PLS) function or as inputs to the High Speed Counter (HSC) function of the controller.
The High-Speed Counter function includes the high-speed input circuitry, the high-speed counter hardware and the firmware and user instructions that configure and operate that hardware.
There are four input points wired to the HSC hardware to support a quadrature encoder input with external reset and hold inputs. Even if you only use a single counter channel, the other inputs are still wired to a single high-speed counter hardware circuit and the MicroLogix 1100 and 1200 do not support multiple HSC functions.
I see my contemplation has cost me the post race.....
Although I've used event interrupts for fast counting, I think they're the wrong solution for accurate frequency measurement.
No, Ken, I think your contemplation has, yet again, resulted in an authoritative response that will help clear the mud for other readers (including me!)
Thanks...
Do i have to use interrupt subroutine, or immediate read high speed input, for Unitronics Samba plc or reading only the correponding register in...
127
Hello Folks, Has anyone configured a Momentum high speed counter on Unity 13.1. We need the wiring diagram for Momentum High speed counter and...
82
Does anyone have any experience with working on piezoelectric motor control? I want to use off the shelf components to hopefully change the...
746
i am bench testing a 1734 -VHSC24 Point I/O High Speed counter module, i cannot find any examples of wiring the outputs from the module. does...
1,398
Hi, I have a setup of one master s7-1200 - three slaves s7-1200 On each of the slaves there is a HSC on a motor for positioning. It generates...
1,087