I have assigned the DIGI ONE 1A for IP 199.64.176.16
How do I assign the IP for the OMRON SYSMAC CPU to recognize the IP address if the DIGI ONE 1A
Thanks
I'm not sure but try this
1-In the project worspace at the left, you have the Plc icone with the model(CS1G) and offline. Double click on that.
2-Under "network type" select ethernet
3-than click on setting.
4-In the pop-up go in driver. You can enter you're Ip adresse there
5- Now try to connect online.
I think that what you are missing is the Digi driver (Realport software, if I remember) that makes that converter on Ethernet appear as a serial port on the PC.
Then you set the programming software (CX Programmer ??) for Host Link communications.
The PLC serial port also has to be set for Host Link communications, matching the settings made in the Digi converter.
I am going to switch PCs and see if I can find the document that I wrote on this setup.