Is it correct ???
DIMPOL
Oct 2002
24
NETWORK 1 // Main Program
// On the first scan, call subroutine 0
LD SM0.1
CALL SBR_0
NETWORK 1 // Subroutine 0
LD SM0.0
TON T37, +50 // Set the interval for the timed interrupt 0 to 5 SEC
LD T37
ATCH INT_0 10 // Attach timed interrupt 0 (Event 10) to INT_0
ENI // Global interrupt enable
NETWORK 1 // Interrupt 0
// Read the value of AIW4 every 5 SEC
LD SM0.0
MOVW AIW4 VW100
Nearly...
It looks like S7-200...
1. A timed interrupt can only be triggered between 0-255ms.
2. SMB34 contains the timed interrupt interval, not T37. Event 10 is timed interrupt 0.
3. If it's a 5 second interval you need, a normal timer will do adequately.
This is from memory so you probably should check. Let us know if you need any more help.
Yes, it's about S7-200, thanks for ansewering. I am truing to measure an analog signal every 5 SEC.
can i do it with FOR/NEXT command ?
can i store the 1000 recent values of the signal ?
I wouldn't use a FOR/NEXT. Investigate the ADD TO TABLE instruction, or I'd use an indirect address pointer, as this would allow better flexibility.
A self-resetting timer calling an SBR works fine.
2004 (ATHENS)
NETWORK 1 // Create table with 100 entries starting with memory location VW4
LD SM0.1 // On the first scan,
MOVW +100, VW0 // define maximum length of table
NETWORK 2 // Reset table with input I0.0
LD I0.0 // On the rising edge of I0.0,
EU
FILL +0, VW2 101 // fill memory locations from VW2 with "+0"
NETWORK 3 // Write value to table with input I0.1
LD I0.1 // On the rising edge of I0.1,
EU
ATT VW100, VW0 // copy value of memory location VW100 to table
IS IT CORRECT ?
IS IT CORRECT TO WRIGHT ATT AIW4, VWO ?
HOW CAN I CREATE A DELAY TO READ THE ANALOG SIGNAL EVERY 5 SEC ?
I am a bit confused, so any help it will be very usefull.
Ôhanks for your time... anybody
BYE
You are doing OK.
EU
EU
IS IT CORRECT ?
Yes, if all you what to do is put VW100 in the table.
Yes, see chapter 10.8 of the S7200.pdf. It says which data types are valid for each parameter.
See chapter 10.5 page 10-17. There is an example of at 300 millisecond retriggering timer which is similar to what you want.
Go to www.google.com. Search for s7-200 manual.
I find some manuals but they don' t hane any example. If you can to post it here, i will be very greatfull.
THANKS
P.S: SORRY FOR MY ENGLISH
Daft question coming up...When I want to modify a value, what's the best/correct way to do this? At the moment, I am entering the value (e.g...
458
Good day. I encountered a problem when calibrating a channel on the IF16H module. The module is located in the local backplane along with the...
756
I have some programs that i received from 1 of our programmers whos installing a new machine in our plant. He added them to a external hard drive...
1,391
Hi, At the moment, If the user fails to provide a valid username/password, the image attached appears "Invalid password or user name. Logon has...
1,598
Hi, In a Direct On Line circuit for CW and CCW operation of a 3 phase motor, what is the right way to interlock the contactors. 1) Use a NC...
1,551