Anybody know how to fix this:
I have a 4-20mA analog output from a VFD going into a non-isolated analog input card (AB 1756-IF16). The VFD unit is powered by 208V buy supplies 24V for the output. The analog input card is also 24V but is powered by a separate 24V power supply.
The card can't read the output from the VFD. I believe the problem is that both devices are trying to power the 4-20 mA signal. Since they are not both supplied by the same source I don't believe I can wire it like a 3-wire transmitter. Anybody know how can I make these two devices work together?
The 1756-IF16 is a joy to wire. Check out the Manual carefully.
Did you tie the Channel Return (iRTN)to the RTN Terminal?
I have attached the Current Wiring Diagram in a Doc File.
Sthompson has it partially correct. The 1756-IF16 does not source loop power, but it can cause trouble if you have different grounds. The basic for current inputs that are referenced to the same supply ground, is to only hook up the In<channel> and the iRTN<channel>, then jumper the iRTN<channel> to the module common. This is the norm for 16 channel mode.
If you do, however, have a problem with commons NOT referenced to the common on the module, you have two possible choices. For 16 channel mode, make sure that the IF16 is the LAST input in the loop (closest to negative), and bond the iRTN, module RTN, and source common together.
For 8 channel mode (differential), in 99% of the cases, you still do not need an isolator for a foreign source supply, as long as it's maximum potential relative to the module ground is less then 100VDC or so (I've gone as high in emergencies as 230VDC, but that scares the heck out of me safety wise). In this case, the module is configured for 8 channel differential mode, the + from the current loop goes to IN-0, the - from the loop goes to IN-1, and you bond iRTN0 to IN-1.
Thanks, rdrast.
I am in 16 channel mode and I currently have 9 other devices on this card (channels 0-8) which all are being powered by the same 24V power supply, thus having the same ground. The 24V common is already connected to the RTN (terminal 28).
So you are suggesting that I connect the positive from VFD output to IN-15, and the negative to iRTN-15 and RTN (terminal 27)?
The iRTN Jumper is required for Current Applications. It ties the open end of a 249 Ohm Resistor to the Common RTN.
I have several IF16 Cards with a mix of 2 wire, 3 wire, and self powered units. i.e. Temperature Sensors, Pressure Sensors, Flow Meters etc.
They are all set up for 4-20mA, and work as expected. I have seen miswiring blow the 249 Ohm resistor (By others).
I have had to replace a bunch of the surface mount 249 Ohm Resistors to get all the channels back up and running.
Stu.....
I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a...
259
I had a question with regards to an Non-Isolated vs Isolated RTD Input Card. This would be for a Flex 1794-IR8 vs Spectrum (1794sc-IF8U or...
1,803
I am stumped. I haven't run into this before. We have a four wire 4-20mA sensor +PWR -PWR +SIG -SIG We have tested it with a process meter and...
17
7,780
I had a customer ask me to investigate what state a digital output would be in a PLC5 if the the processor faulted or was put in program mode...
1,188
Hello, I am wondering if anyone out there has any experience with running a type 2 hypervisor for a programming computer that is isolated from the...
1,817