Dear experts,
I am using a Thermocouple K type and connected to a SM 1231 signal board (6ES7 231-5QD32-0XB0) controlled by a S7-1200 PLC.
In my hardware configuration I have set the my signal board to Thermocouple, Type K, degree Celsius. I was supposed to read my temperature on the IW inputs already in degree celsius and divide them by 10 according to the manual to get the final value.
But I am getting a constant value 65534 which I found out to the double of 32767 the value one obtain when invalid data is received on the channel. I am at room temperature. At a certain pointing time it seemed to work fine and gave me right temperatures. Suddenly it changed again and since I am only reading these strange values 65534 on my two connected channels. I am suspecting the wiring but I can't find where the mistake is exactly.
Can you please assist me with this? As I am busy commissioning a plant and this is really stopping me.
Your assistance, will be much appreciated!
Kind Regards,
Sonia
I don't know Siemens but a full scale, upscale value typically indicates thermocouple burn-out, which is when a thermocouple analog input is an open circuit.
Driving the indicated/reported temperature upscale (or downscale, depending on configuration) is a visible flag that something is wrong, and when the thermocouple temperature is an input to a heating control loop using reverse action, the control output will drive to zero to avoid putting energy into control loop whose process variable is an unknown.
I'd recheck the wiring.
Have you used thermocouple wiring and thermocouple connectors between the thermocouple and the 6ES7 231-5QD32-0XB0? And is your thermocouple of the type 'isolated'?
Sounds like the thermocouple opened up on you, you should check your continuity with a meter.
Hello, Hoping you guys could help solve an issue I'm having with a Siemens KTP1200 Basic HMI. I've been onsite for a few days making changes and...
680
Hi All, I've been able to get the OPC UA Client driver on a TP1200 comfort panel project communicating with a Kepware OPC UA Server on a remote...
6,425
Hi! I have a strange problem I can't come up with a solution to. I have a TONR in my program set at 7 minutes. When the timer reaches 7 minutes...
2,347
I've encountered an issue with a Digi One IAP Serial-to-Ethernet Bridge connected to a Micrologix 1200. It's been operating for several months...
4,251
I'm using a S7-1200 1214 CPU with version 10.5 TIA software to control a chilled water loop- but even with compact PID instruction enabled and...
2,732