Hello everyone,
I am currently using an Allen Bradley 2080-RTD2 Module for the LG Ni 1000 Sensor. Unfortunately I can't get any reading from the PLC.
The module is only capable of supporting the following sensors
100 Ω Platinum 385,
200 Ω Platinum 385,
500 Ω Platinum 385,
1000 Platinum 385,
100 Ω Platinum 392,
200 Ω Platinum 392,
500 Ω Platinum 392,
1000 Ω Platinum 392,
10 Ω Copper 427,
120 Ω Nickel 672,
604 Ω Nickel-Iron 518
I was assuming that I can still get a reading regardless of the type of the sensor.
My question is do you think that the RTD module is not capable of measuring the LG Ni Type Sensor?
Thank You.