Member
Your areas are mapped together in the Master DP configuration.
In that example Master QB40 ==> Slave IB40
and Master IB40 <== Slave QB40.
You can address what you like, it could just as easily be QB120 ==> IB2.
The example Siemens gave shows how an input in on PLC is passed to an output of the other PLC .... VIA .... the DP mapped I/O.
In that example Master QB40 ==> Slave IB40
and Master IB40 <== Slave QB40.
You can address what you like, it could just as easily be QB120 ==> IB2.
The example Siemens gave shows how an input in on PLC is passed to an output of the other PLC .... VIA .... the DP mapped I/O.