When setting up a generic ethernet module in RSLogix you're required to enter a number of configurations parameters like the ones shown in the attached image. Can anyone tell me what each of these numbers mean? What is an input assembly instance, an output assembly instance, a configuration assembly instance, and their associated sizes?
Strictly speaking it's all laid out in the CIP Specification, but just telling you to read up on the object model isn't terribly helpful. I'll try to simplify.
An "Assembly" is a data object built up out of smaller data objects like BOOL, INT, DINT, REAL, etc. I/O connections are generally made to an Assembly object.
There can be more than one Assembly Object in a device. There might be one for basic I/O, and a different one for advanced functionality.
The most common Assembly Objects are 100 and 101, but it's largely up to the vendor.
The documentation for the EtherNet/IP device should have a little table or chart showing what each bit or byte in the Assembly means.
"Input" and "Output" are from the ControlLogix perspective, here. The "Output" assembly is data that the ControlLogix produces, the device consumes, and the device then applies to its output functions.
The Configuration Assembly is setup information that's sent to the device when a connection is made from the ControlLogix, usually at powerup. This is frequently not used, so they just make the Size value zero.
Hello, in one datasheet about analog DC alarm device I have found (among other infos) these informations: 4:Supply voltage 24 VDC (cross...
1,769
Hello: One customer has an application using 1715-IF16 on EtherNet/IP for the Rockwell side and HART master for the sensor. Everything is OK and...
1,805
This is in an existing application, so stuff I've found and I'm trying to debug. I've got no Tech support contract, so can't view Tech Notes :/...
1,564
Hey guys So when im online and i look at my tag list Some values show up with a white background some show up as grey What is the difference...
1,186
Hi, Can some explain me what's the measining of this option inside hardware configuration. When should I want/need this option to be...
2,924