Micro850 - MSG_CIPSYMBOLIC
Cyanogen
Jul 2021
TX
I have 2 Micro850 PLCs that I am working on that use MSG_CIPSYMBOLIC blocks to transfer data back and forth. Or at least they were...
Basically the project was a simple IP address change on each controller to add them to a different network. After changing the IP address on the controllers, and inside the MSG_CIPSYMBOLIC block, the program no longer functioned.
I've checked network cabling, IP addresses on the controllers, and inside the MSG_CIPSYMBOLIC blocks, and everything looks correct. Rockwell Automation has been less than helpful, and won't return calls/emails so hopefully you guys could point me in the right direction.
I don't mind getting someone on an hourly support gig if needed, just need to work this problem out.
Obvious stuff:
You already did this, probably, but have someone else look at the IP address settings; perhaps there is a typo you are not seeing, because you are seeing what it should be and not what it is.
Can you look at network traffic with Wireshark or similar?
Was it only the MSG_CIPSYMBOLIC instructions that no longer work?
Can you upload the program to ensure the new IP addresses are in the programs that are actually running?
A few weeks ago (one of the only times I could get Allen-Bradley on the phone) they remoted into my machine and double checked the IP addresses and told me they looked fine.
It's only the MSG_CIPSYMBOLIC instruction that no longer works. Everything else seems to be functioning as intended.
I have uploaded the programs from the controllers, and the correct IP addresses are in the programs.
Here are the programs in question:
https://drive.google.com/drive/folders/1BgRHgDNNXCMS2EIiMgVNYlpBoWZm1pYA?usp=sharing
Do you have copies of the original programs, the ones that worked?
The IP addresses look good to me. One of those programs has two message instructions; I assume that is an attempt to debug?
The elements have the following values:
  • CL2
    • CommsSymCfg.Service := 1 (Write)
    • CommsSymCfg.DataType := 200 (UDINT cf. here)
    • CommsSymCfg.Symbol := 'CommsDataOut'
    • CommsSymCfg.Count := 5
    • The Data buffer input to the instruction is
      • CommsData
        • a USINT array [1..10]
  • LAS
    • CommsSymCfg.Service := 0 (Read)
      • ComData
So the .DataType and .Count values are 200 and 5 in both programs, indicating five UDINTs for a bytecount of 20 (=5 x 4), but the Data buffers are only 10 bytes long. Could that be a problem?
The original symbol data type was 198.
This is what is confusing me... The facility maintenance swears these systems were working, and I believe them because the chemical feed was working on the trending section of their SCADA system.
This is my first time working on a project through Connected Components Workbench, so I'm not sure if I made a mistake in uploading from the controller because the LAS program has the MSG_CIPSYMBOLIC parameters in it, but the CL2 program does not.
Any advice or tips would be greatly appreciated!
Hi, Iam Working in a project where Micro850 and Epson ROBOT is there, I need to read and write bits to and from ROBOT. Iam Using TCP/IP and...
1,285
Hi everyone. I'm trying to read values from a Loadcell with a 2080-TC card. I know the 2080-TC is a thermocouple card but it reads millivolts that...
244
Hi everyone, I am working with micro850, a proximity sensor (FOTEK, PL-05P) and a 3DOF serial arm robot. I use MC_MoveRelative to control the...
122
HI everyone! I am trying to use a Micro850 to control a SureStep (Leadshine) Stepper drive (DM805-AI) from Automationdirect. I have no trouble...
217
Hi guys, I have had some issues with uploading a program from a Micro 850 PLC. This is the first time connecting so I don’t have a file on my...
411