e27978 said:
Thanks for all the help changed the osr to ons. With no errors.
I beleive I will not exceed the current rating of the outputs.It controls a mac valve bank with five valves four opperating at 8.5 watts 24v . One opperating at 8.0 watts 24v . If I figured this right that should be 1.74 amp. At the most there are three active at one time.
8.5 watts at 24 volts will be 0.354 amp...the TRIAC rating is 0.500 amp (usually...check to be sure).
Because they're inductive loads, I would make sure the Mac solenoids have built in surge suppression, and if not, add some just to be safe.
The mac valves do not have built in suppression would these be added at the mac valve . I am not sure but would these be the correct ones 199-FSMA9
For transistor outputs to soleniods the OB8 card is 24vdc, right?
You will be able to help it's life by adding diodes reversed biased in parallel with the load...then they provide a path for the reverse current cause by a collapsing magnetic field when the inductor (solenoid) is turned off.
For AC triac outputs, a surge suppressor is more applicable...but I think all you need are the diodes...
They can be added to a terminal strip. I have in the past, added them neatly by re-arranging the terminal strip to match the spacing of the diode leads, add some tiny heatshrink to them and clamp them in the terminal blocks.
Processor changed and running no problems
Rearranged terminal strips and used the dioads
This should greatly increase the life of the processor
Thanks to everyone who helped
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
134
Hi all, We have a very old pit pump system running on Micrologix 1000. Now, whenever there is an alarm for high conductivity, we want that alarm...
1,258
Looking at a Micrologix 1000 1761-L32AWA, I tried to connect using the 1761-CBL-PM02 through a Serial to USB converter (This setup was used...
986
Hello All I am trying to convert a ML1000 program for use in a ML1400. I didn't create the original program & documentation is non existent...
4,414
Hey Folks, I have a customer with an older machine that is controlled with a MicroLogix 1000. The machine just quit working. The power light is...
22
10,569