micrologix 500 intructions
stu
Aug 2005
England
786
good day to you, i am new to plcs i have been given a project at work to take out a automation direct plc and replace it with a micrologix 1200 there is a part of the auto programme which has a set and reset function but i dont know how to do it on the micro can anyone help? it might be me being thick
thanks
stu
Ken Moore said:
Latch (OTL) and Unlatch (OTU) are the AB version of set and reset.
Be warned, latches are retentive and will not be cleared on a power cycle.
Hello Sir,
I'm new at this, so i was thinking of asking ur advice on this.
u mentioned latched n unlatched will not be cleared on a power cycle. What does a power cycle means? does it mean that even if i switched off the plc and restart the latched output is still there?
Regards,
Al
alearon said:
Hello Sir,
Regards,
Al
yes
Each PLC mfg or PLC model will be different. Check the programming manual for the model you are working with. (Sorry, I can't give you a direct answer about the Mitsubishi).
Ken Moore said:
Mitsubishi PLC's depend on the configuration. However, I believe the new PLC's have a set and reset instruction as well. It's been a long time since I worked with Mitsubishi PLC's, so my information may be incorrect.
See this thread on another board:
http://forums.mrplc.com/index.php?showtopic=10109
Hello sir,
from the sample programs that i have, yes Mits do have set n reset functions. From the automation that i have, latched input will be refreshed when powered off.
Also i read through the thread u adviced and found out that they use M500 above as latched relays. do they mean that i can use m500 and above instead to replace the SET function?
I understand that you didnt work with Mits for a while but i'm in desperate need of a guru now..heh heh.
Thanks.
Al
hi
so with rslogix 500 (micrologix 1200) how do you set and reset contacts safely?
stu said:
hi
The way I do it is to make use of the first scan bit. I used it to clear all of my latches and take the machine to a safe state when power is turned back on. S:1/15 is the adress. This bit is on for the very first scan of the PLC only. This applies to SLC's and Micrologix.
Generally I will only latch bits. I try to group these bits to gether as much as possible so on the fist scan I can do something like this
--[S:1/15]---------| CLR |
|B3:0 |
This way I do not have to create an unlatch for each bit I just clear the entire word.
130
Hello, I have a 1764 1500 LSP Series A that keeps failing with DTL_E_FAIL I/O error. Searching around it seems there's a weird issue specifically...
125
I'm not super familiar with the Micrologix line of processors, but I am pretty familiar with RSLogix 500. I'm trying to simply copy a string to...
323
Good Day i Have Micrologix 1500 LSP, and I want to get data from plc and send it through Modbus RTU slave; I have only ch0 on that plc I Order...
947
Hello folks, Hope everyone is doing fine. I got an OMRON NS10-TVOOB-V2 hmi screen last day and planning to use it with Micrologix 1500. 1. Is...
1,226