Micrologix1500 can i vary an output voltage from a prox?

That's because the word address O:1.0 is retentive. If you want it to go to zero you are going to have to move a value of zero to it.
 
Last edited:
Thanks Mickey for the advice. This is the first time I have ever used a MOV control, analog card, or a integer. So I am pretty lost. You said I needed to add a 0 to my O:1.0 I tried many times but I couldn’t get it rite I’m sure its me. Any more help on where to put the 0. also I’m unsure if you red the whole post I still haven’t even hooked up my prox. And I know without help ill never be able to tie it to my output.
 
you will need to look a the SCP instruction
to accurately control the Analogue card
have a read of the help command -
 
I am not sure what you are trying to accomplish but see picture below.

If the trigger is true then whatever value is in N7:0 will be moved to the output word ( O:1.0). If the trigger is false then a value of zero (0) will be moved to the output word ( O:1.0)

move_zero.png
 

Similar Topics

Hello everyone I have a micrologix1500 connected with RS232 to my computer, and connected to the 1761-net-dni with a series connexion from the...
Replies
4
Views
2,936
Hello Everyone, Let me start out by saying I am definitely not a pro by any stretch of the imagination. What I have is a Micro850 that is on the...
Replies
2
Views
2,714
Okay so I just went into my ML1500 and mistakenly changed a comm setting for channel 0 or 1 channel config section of the programming software...
Replies
2
Views
1,187
Hi, I have a Micrologix PLC 1500 on which channel 0 is free. I need to take this PLC in scada via ethernet module any one can suggest a suitable...
Replies
1
Views
1,525
Greetings! One of my shop's Micrologix 1500 processor's mode selector switch(soldered on the PCB) has broken off. Currently, it is stuck in RUN...
Replies
2
Views
2,385
Back
Top Bottom