Micromaster 440 on Profibus
YoungWint
Dec 2012
East Midlands
77
Hi All
I have a project with a MM440 drive on profibus.
What I would like to do is select it into two modes of operation via a selector switch as follows:
DIN1 - Manual
DIN5 - Off
DIN2 - Auto
DIN6 - Aux. Run
DIN3 - EStop
DIN4 - EStop
So far I have been able to get the drive to start and stop via either the switch or profibus.
The issue I have is that in manual to setpoint needs to come from the BOP and in Profibus from the PLC. I dont seem to be able to configure duel sources for the speed.
Anyone advise?
why don't you use a changeover relay to switch from where the reference come. put main reference on NC, aux on NO and COMM to AI of VFD.
that would be on-the-fly suggestion, for other solutions i'd heve to check the manual, but since VFD's have only two built-in inputs, and i assume one of them is taken for process feedback then i don't see anything else.
Configure two comand data sets (CDS) one for auto and one for manual. Change CDS with auto/manual swithch. Check parameters p810 and p811 for this.
p1070(main setpoint)source should be set to profibus control word (p1070 = 2050) when in auto and to MOP(p1070=1050) when in manual.
check p840 - for ON/OFF1 command source.
p844/p845 for OFF2 source.
P848/p849 for OFF3 source.
My tutor asked me for this small project: using S7-200 control MM440 with PROFIBUS. Because S7-200 with PROFIBUS module EM277 can only be PROFIBUS...
2,986
I am working on converting from a seimens micromaster 440 communicating by profibus to a Schneider Electric altivar 71 communicating over...
1,201
I am getting a fault code F0022 (2) on the drive. Has anyone ran across this.
4,203
Hi, I have an intresting problem: I replaced a mocromster vector drive with micromaster 440 which was running on profibus. I made the hardware...
2,596
Hello all, We have a MM440 and 2 limit switches and one rotate encoder. And the MM440 is on profibus-dp. The encoder will tell the position so...
2,273