I have a query regarding communication between Mitsubishi FX2N PLC & HMI EZS6M-R from automation direct.
Mitsubishi plc has two ports one is RS422 for programming and other is RS232 ,RS485 or RS422
I am trying it on programming port RS422 and melsec FX-REV-E protocol , but its not working
Does it require any PLC com port setting for hmi communication in plc program if yes how it will be set plc com port.
Which port is used for normal hmi communication.
You cannot configure communication parameters for the PLC port.
Try to match the ones of the HMI with the PLC:
7-bit word, 1 stop bit, 9600 baud, even parity.
And what is your communication cable?
Is the HMI port RS232 or RS422?
i configured HMI parameter as 7-bit word, 1 stop bit, 9600 baud, even parity, still not communicate , is there any setting for to make master PLC.I am not aware of melsec FX-REV-E protocol is full duplex or halfduplex
How to connect Fx2n PLC to Barcode reader
I have Fx2n PLC.I want to connect barcode reader with it.
can any one have program for that..and also how to connect barcode reader with my PLC
Try mitsu website for cables and info for your app. If you get an Mitsu or Beijers HMI, you can go through transparent mode which allows you to program both at the same time.
Dear all, I have a FX2N-20MR chinese semi-clon of a Mitsubishi PLC. It has only a serial DB9 port that cannot be removed or exchanged (which is...
2,082
Hi everyone, I am new here and this is my first post. I've just received my new PLC by post. It is a FX2N-20MT, a chinese clone of a Mitsubishi...
28
18,400
good morning every one I have a problem in Mitsubishi plc fx2n the battery led is on and progE/cpuE led flashing the plc in a machine which runs...
2,047
For some background information, I am in the process of converting a Mitsubishi FX2N to a Siemens S7-1200. I am viewing the Mitsubishi program...
2,831
Hi Dear friends, My Mitsubishi PLC FX2N-80-MR has stopped working and Prog-E led is on.What Can be The reason.Please guide. Urgent. thanks In...
6,622