ML1200 RSLinx Comms settings.

Honga

Member
Join Date
May 2010
Location
Aus
Posts
316
G'day forum!

I'm running a 1762-L40BXB (MicroLogix 1200).

My issue today is that when I connect using my serial cable (Works on a 1000 and 1100) and try to configure the driver in RSLinx I get the notorious "Unable to verify settings" etc.

See http://www.plctalk.net/qanda/showthread.php?t=8941

I know that the issue is not the:
Computer
Cable
Port Settings

My MicroLogix 1200, unlike the one mentioned in the linked post, only has one serial port next to the trimpots.

I am getting a fault flashing, but no way to pull the code.

If any of you have found a resolution to this and could help me out that'd be much appreciated.
 
Fixed!

Was that I wasn't getting a good contact on the comms reset button.

Used a paperclip. TOo easy.
 

Similar Topics

Hey all! Long time reader, first time poster! I have an EA9-T7CL and an MicroLogix 1200 connected via DF1. I'm all good and got everything mostly...
Replies
3
Views
652
Hi every master,Recently i met a fault about 1762-L40BWA 1,When i get the PLC, The Fault light is lighting, I am not remember the fault message,I...
Replies
0
Views
718
Hello everybody and master,I met a problem about ML1200.It is described as below: 1,When i got this PLC,The FAULT light is lighting, My computer...
Replies
4
Views
1,111
I had planned to use PTO instructions to control a servo motor, single axis only. We have a ML1200 BWA model. According to the ML1200 manual...
Replies
7
Views
3,491
I am using Modbus to read 36 registers from a ML1200. 2 of those registers are suppose to be L11 data and 2 of the registers are F8 data. Long...
Replies
3
Views
1,391
Back
Top Bottom