Combo, do you mean the Y capacitor placed over the mains supply contacts? If that's the cap you're referring to I would say: don't ever remove it unless you're replacing it with an X cap. That type of Y capacitors are intended for noise reduction. The Y class is somewhat less robust than the X class.
If you mean something else: please clarify.
Kind regards,
Hi
The Y Capacitor, in the manual they say that u have to remove it.
Brugje wegknippen om MM440 op IT net te laten werken. In the manual they say to remove it ?
Combo,
it seems Siemens uses their own definition of a Y capacitor. I had to search the manuals to see what you were talking about.
The capacitor mentioned is a capacitor assembly (consisting of three capacitors): one X2 class capacitor connected between the line and neutral and two Y class capacitors, one connected between line and earth and one between neutral and earth. Earth is here mentioned to be the earth connection of the drive.
If you don't remove the connection between these Y capacitors and the earth terminal and you are not connecting the earth terminal to an earth connection, it will result in :eek: a very dangerous situation if you touch the earth terminal.
Remember: capacitors DO tend to let AC current pass.
Kind regards,
We have a mm440 drive that is not starting remotely in automatic. We can control the locally when in hand mode with 0-10v potentiometer. When we...
1,381
Hi all, i m new to this forum. i recently had an assignment where the user wanted to copy parameters from Siemens Micromaster 440 using BOP. Help...
5,822
Hi, I'm using PPO1 to communicate with MM440. I only need to read and modify MM440 parameters, so i sucssesfully use PKW mechanism. I don't have...
1,312
Dear all, Could you please help me a bit? Please check the attached pictures. PIW582 is the signal from the MM440. Act. Filtered torque. In the...
1,498
Sir, I have Siemens mm440 drive .which is using for conveyors .it's speed is controlling through pot (analog input 0-10 volt) But i am facing...
44
11,316