i am trying to set up comms between a modicon m340 and a modicon m168 controller. I am using the mbs1 connection on the m168 to the modbus port on a p342020 modicon m340 plc. All i am trying to do is take 5 analog signals into the m168 and send the values to the m340. I am doing this because the m168 has the ability to take thermistor inputs directly into it. I will also be using the m168 to talk bacnet to 4 chillers with a bac/net mstp module. I have tried to setup the m168 to send the info to the m340, but obviously without success. I have attached the m168 program for an example...
I looked at your program and see that you have not exported any values to the Modbus interface. Click Tools -> Export Entities..., then drag the variables to the address that you want the data in. Address 1 under Register Vars would be 40001, address 1 under Digital Vars would be 00001. See attached, I set up a few for you as a go-by.
Another thing that is incorrect - MBS1 is slave only and you're trying to use it as a master on your MODBUS_COMMS sheet. If you want to be a master then you must set up MBS2 as Modbus Master and do it from there.
Hey all, I am having an issue concerning the Modicon System Responsible for the operation of our Generator System. (Particularly Dresser-Rand...
2,561
Hello, I'm having a hard time understanding how to get a Modicon M340 to pull a Modbus address from an ABB Totalflow via Ethernet. I set up a port...
1,155
Hello. New to Unity and had a couple quick questions. Can a Modicon M340 output to a small multiline LCD screen and not a full HMI?
967
Hi, I'm configuring the M340 controller with ATV320 inverters via Canopen. Everything was fine until today, when after starting the electrical...
1,337
I've got an M340 hitting an Ethernet to Serial converter one read at a time. Each read is enabled through a one-shot r_trig. I've got some extra...
1,597