Moving a EE Prom from SLC 504 to 503
debeuu2
Jun 2014
Georgia
17
I got a failed SLC-504, swapped out with a on the shelf 503. Not sure if my files are latest/greatest from the original 504. I swapped the EE-Proms, but the 503 LEDs go to nothing after the swap out. Both Proms are a M11. Please help.
Thanks Dravik. The 5/04 is completely gone. The OEM told me it was possible, so I tried, to no avail. I dumped the latest program file on archive, and is working less the last 10 years of tweaking, that we will have to begin again. Thanks for the help.
The LEDs being off (except for the power supply) would be normal. Be aware that the program does not automatically transfer on power-up. It has to have been originally saved that way to the EEPROM module. So your 5/03 is just powering up normally.
So what is in the 5/03 is whatever was in there the last time it was powered off (or it is empty). See if you can go online with the 5/03 and then use the RSLogix software to transfer the project from the EEPROM to the 5/03 memory. Look under the Communications menu. If I recall correctly that is where the option is found.
If you cannot go online with the 5/03 you can create a new empty project and download it to the 5/03 and then go online. Then transfer your application from the EEPROM to the controller.
The memory module is certainly compatible and when you load it you will get messages about the wrong CPU but it will offer to correct that setting. Be aware that any communications or networking obviously won't work since it uses a different type of network. And, as long as the project will actually fit into the (likely) smaller memory of the 5/03, it should be good to go.
OG
Hello, We have one customer who is asking if there is a way with Allen Bradley to restore the EPROM to RAM easily by some method such as turning...
7,520
All, I am trying to reset timers when a Work Order change occurs. The Work Order comes in as a string and I am comparing it to a tag...
60
I'm a Siemens person, and this is one of my first AB programs. The customer wants everything programmed in Ladder. I have a lot of data (3...
241
Hello, I have a compact Logix plc and I have been task with configuring alarms into our SCADA when an Analog signal stops moving. The analog...
260
Hello, i am a beginner with a Siemens Logo 8 PLC. I would determine the direction of an object if it passes a whole cycle of 2 input sensors. See...
199