One thing to keep in mind is that flow through a ball valve is not linear with % open. This will affect your tuning, and you may have to live with slow response to avoid hunting.
Here’s something you might consider.
Say you’ve tank A and tank B with respective levels and valves.
Make a split-range PID with output as follows:
0% (A 100% open, B 0% Open), 25% (A 100% open, B 50% Open), 50% (A 100% open, B 100% Open),
75% (A 50% open, B 100% Open), 100% (A 0% open, B 100% Open)
The input to the PID is (level B – level A) with a range of -100 to 100, action is direct acting. Tune this with mostly proportional action and a very small reset value.
Nominally, you’ll want a setpoint of 0.
Let us know what happens
This sounds good to me, however I am not sure of how to go about making a "split-range PID". I understand conceptually what your saying, and it actually is straightforward. But how to get one PID (PD) to output control to 2 different valves...I have an analog 4-20 output to control each valve. SO it is a matter of getting,...what...say 0 to -100 to equal the 4-20ma of one of the valves...hmmm
B%Open = Min(2*PID_output, 100)
A%Open = Min(2*(100 - PID_output), 100)
...and you'll have a little more manipulation for fail-open...
Heed Mr Jenkins' warning... maybe can read up on what action positioner is used... characterizers are an option but a bother...
I do like the mechanical solution posted by others.
Goof luck and let us know what happens
Hello, I had a question about benchmarking the Rockwell FactoryTalk View SE software. I've installed in the neighborhood of 30 different...
285
Hello, I'm trying to test Acopos multi using Automation Studio. Ready LED is green blinking, how can i know what error of Acopos on Automation...
136
Good Afternoon , I'm sure there are many Ishida Muti-Head Weigh Systems . We have a Ishida CCW-M-214W Multi-Head system . We are...
547
Hi Guys, I'm trying to integrate Pilz Ethernet IP Module to ControlLogix. I added Pilz module as a Generic Ethernet module and I'm able to...
514
Good Morning , We have a Ishida Multi-Head Scale . I had experiece with them for chips , crackers , etc. , but now we are using them for...
469