Multiple Comm paths factory talk view ME V6.1
DUNK
Aug 2006
south carolina
83
I have no problems setting up a single communications path In FTV ME. How would you go about setting up 1 application to communicate to multiple PLC's via Ethernet IP?
It would be the same..meaning just add the shortcut and point it to the controller and repeat.
HTH
I must be missing something. I added each controller, all have different names. When I Clicked OK it only tells me of the one change and not all 3.
Add your shortcut and then select the controller and then select apply and repeat. I also think you when your all done you may have to hit verify and ok in the lower right hand corner but that could be just a habit of mine.
Hello, I have 3 drives setup in a daisy chain off of 1 22-comm-e card. The daisy chain has 120ohm terminating resistors at both ends. For...
1,823
This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
146
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
496
I have 9 field devices, three METSEPM5110 power meters and six ACE949-2 rs285 interface modules. I want to read this Modbus rtu data through rs485...
317
I'm trying to use DTM browser to make make modbus poll from RTAC. I'm able to get the points in first poll object. But not able to get anything in...
127